  1. I think I know the answer to this but....
    I’m looking for a new compressor and the one I found the tag on it says 208/230 volt and Amp draw of 23/21. My current one says 240 volt and 14.0 amps. The breaker switches in my electrical panel says 20 on it. So do I need to change out the breaker with a higher amp switch? (I wouldn’t do it myself)
    Thanks
     
  2. Halfdozen
    Joined: Mar 8, 2008
    Posts: 630

    Halfdozen
    Member

    I'm gonna guess the 208/230 volt unit is three phase, which is industrial power. It won't run on residential power, which is single phase (actually two phases of 120, for a total of 240 volts). Check the spec plate on the motor for number of phases.
     
  3. It does say the new one is 1 phase.
     
  4. Halfdozen
    Joined: Mar 8, 2008
    Posts: 630

    Halfdozen
    Member

    Then if it's 21 amps continuous at 230 volt, I'd put it on a minimum 30 amp breaker, so the startup surge doesn't pop the breaker.
     
  5. banginona40
    Joined: Mar 5, 2007
    Posts: 778

    banginona40
    Member

    If you go with a 30 amp breaker you will need #10 wire.
     
  6. Thanks for the info.
     
  7. That amount of amperage draw indicates a less than quality motor.....
    the 14-15 amps your current compressor motor draws is more inline with normal.
    A good 220 single phase motor should not require that amount even momentarily at startup......
    all that is assuming Canadian method of ratings of amp draw are similar to USA.
     
    Last edited: Jan 3, 2013
  8. lawman
    Joined: Sep 19, 2006
    Posts: 2,665

    lawman
    Member

    That is some great info fellow's !!!! Thank's
     
  9. mike in tucson
    Joined: Aug 11, 2005
    Posts: 536

    mike in tucson
    Member
    from Tucson

    21 amp draw at 230 is a 5 hp motor. His older compressor is probably a 3 hp motor so it draws less current.
     
  10. Rusty O'Toole
    Joined: Sep 17, 2006
    Posts: 9,756

    Rusty O'Toole
    Member

    Don't put in a heavier breaker unless you install heavier wiring to match. Too much current draw will cause the wiring to overheat and possibly burn or short out. The breaker or fuse is in there to prevent such problems. If you put in a heavier breaker you will negate the protection.
     
  11. Dane
    Joined: May 6, 2010
    Posts: 1,351

    Dane
    Member
    from Soquel, CA

    I would try it as is first. If you keep tripping the breaker, then spend the $ for an electrician to add a 30 amp breaker and required wires size upgrade as stated above. It's very possible it will work with no modifications.​